[Shop-talk] Annealing Copper bars

Donald H Locker dhlocker at comcast.net
Sat Aug 8 16:01:48 MDT 2020


Oops; DifferentialCorrection should be (Kd * DifferentialError)/tPeriod;
but it's not a big deal, since tPeriod should be constant anyway.

Donald.
--
*Plain Text* email -- it's an accessibility issue
() no proprietary attachments; no html mail
/\ <https://www.georgedillon.com/web/html_email_is_evil.shtml>

On 2020-08-08 5:51 p.m., Donald H Locker wrote:
> PID theory can be very obscure. PID implementation is rather simple.
> (And I hope I don't have _too_ many typos below; it is not code-checked,
> but the basics are there.)
> 
> Note that in the pseudo-code below, Error terms are in units of the
> controlled variable (e.g. degF or furlongsPerFortnight or PSIG); the
> Correction and Output values are in per cent. Heaters usually only add
> heat, so the output would range from 0% to 100%; something like a motor
> might have a reversible controller and could use -100% to +100% as its
> control, so the MIN_OUTPUT would be changed to be suitable.
> 
> The entire PID algorithm is fairly simple; most of the control should
> usually be Proportional - bigger error -> bigger correction. The
> Integral correction is to help correct for long-term errors, while the
> Differential correction helps damp oscillations of the Proportional
> correction and tends to reduce overshoot for quick changes.
> 
> To "tune" the PID, start with Ki and Kd set to 0.0, and set Kp to a
> value that is equal to your maximum output error / 100. For example, if
> you want the controlled variable to be no worse than 10F, Kp would be
> 0.1 to start. (This is probably way too large because it means the the
> heaters will be on 100% if the temperature is more than 10F off, but
> it's a place to start.) By increasing or decreasing Kp (I usually adjust
> by a factor of 1.4 each time, so every two changes give a factor of 2),
> you'll find a value that gives stable output, though the controlled
> variable will probably not be very close to you desired set point. If Kp
> is too large, the output (and your controlled variable) will oscillate
> at the "natural frequency" of the system you are controlling.
> 
> Now comes a little magic - add some Ki (start with about 10% of Kp) and
> watch the control. It will (eventually) get the controlled variable very
> close to your set point, but it might be slow. If Ki is too large, you
> will get slow oscillations - time to dial it back until those stop. If
> it seems sluggish, increase Ki until you see the oscillations, then back
> off again until it seems stable.
> 
> Do a similar tweaking with Kd, though if the Kd is too large, the output
> will be "twitchy" - kind of like fast oscillations. This is harder to
> describe, but I hope that gives you the concept.
> 
> ============== pseudo code below ================
> 
> const double MAX_OUTPUT = 100.0; // output is in per cent
> const double MIN_OUTPUT = 0.0; // reversible motors could use -100.0
> const double tPeriod = 0.100; // we'll use 100ms for example
> 
> static double IntegratedError;
> 
> // Tuning settings:
> double Kp; // = Proportional "gain" (a settable constant)
> double Ki; // = Integral "gain" (another settable constant)
> double Kd; // = Differential "gain" (one more settable constant)
> 
> // Initialise everything except the gains to 0.0 at the beginning
> // of time, then get the SetPoint, and the ActualValue,
> // call the PID_loop() function and send the return value to the output
> 
> double PID_loop (double SetPoint, double ActualValue)
> {
>    // During the operation, the following calculations are performed at
>    // regular intervals (1sec or 100ms or faster, depending on how fast
>    // the system you are controlling)
> 
>    double PreviousError = CurrentError;
> 
>    double CurrentError = SetPoint - ActualValue;
>    IntegratedError = IntegratedError + CurrentError;
> 
>    ProportionalCorrection = Kp * CurrentError;
>    IntegralCorrection = Ki * IntegralError;
>    // make sure the Integrator doesn't continue to + or -infinity!
>    // (IntegratedError is the only variable with long-term memory
>    //  so it's the only one with this particular patchup)
>    if (IntegralCorrection > MAX_OUTPUT)
>    {
>       IntegralCorrection = MAX_OUTPUT;
>       IntegratedError = MAX_OUTPUT/Ki;
>    }
>    else if (IntegralCorrection < MIN_OUTPUT)
>    {
>       IntegralCorrection = MIN_OUTPUT;
>       IntegratedError = MIN_OUTPUT/Ki;
>    }
> 
>    DifferentialError = CurrentError - PreviousError;
>    DifferentialCorrection = Kd * DifferentialError;
> 
>    NetCorrection = ProportionalCorrection
>                  + IntegralCorrection
>                  + DifferentialCorrection;
> 
>    // make sure we don't return invalid corrections
>    if (NetCorrection > MAX_OUTPUT) NetCorrection = MAX_OUTPUT;
>    if (NetCorrection < MIN_OUTPUT) NetCorrection = MIN_OUTPUT;
> 
>    return NetCorrection; // this is the PID output
> }
> ============== end of pseudo code ================
> 
> *Plain Text* email -- it's an accessibility issue
> () no proprietary attachments; no html mail
> /\ <https://www.georgedillon.com/web/html_email_is_evil.shtml>
> 
> On 2020-08-08 2:36 p.m., John Innis wrote:
>> Sure be glad to have more info. I have done a lot of arduino projects,
>> but have been finding the PID theory a bit of a tough nut to crack.
>>
>> On Sat, Aug 8, 2020 at 1:19 PM Jack Brooks <JIBrooks at live.com
>> <mailto:JIBrooks at live.com>> wrote:
>>
>>     John,____
>>
>>     __ __
>>
>>     Agreed.  I built a PID Controller setup for my smoker using a Inkjet
>>     106-RL.  It’s a great way to go.  Now I just need to find a kiln.  I
>>     can provide some good info if you are still working on it. ____
>>
>>     __ __
>>
>>     Yes, aware of issues opening a 900°F oven.  ____
>>
> 
> [snip]
> 